Metering calculation question
cdw238
Recently had a 480Y/277-volt, three-phase, four-wire feeder metered for one week. The following were the maximum load readings at each of the phases metered at 277-volts each.
Phase A (metered voltage 277-volts): 356A, 99.5 kVA Apparent Power
Phase B (metered voltage 277-volts): 309.5A, 85.7 kVA Apparent Power
Phase C (metered voltage 277-volts): 331A, 92.3 kVA Apparent Power
Power factor was right around 0.85 for each phase.
What is the correct way to calculate the overall load on the 480Y/277-volt system?
If I add together the three values for apparent power, I come up with a total of approximately 277.5 kVA for the 480-volt, 3-phase, 4-wire feeder which gives me approximately 333.8 Amps. I get this by the following:
227.5 kVA / 480-volts/ (sqrt of 3)
Is this correct?
markstg
Big Easy
Is this correct?
the overall maximum load on the system is 277.5 KVA as you have shown. But the current value of 338.8 A is the average amps of the system, as your measurements show A phase takes more, the others less. If your trying to add load, be careful about overloading phase A, even though phase B and C may not get overloaded.