When the blower goes out and the compressor keeps running why would you think the unit would have a high head pressure? The head pressure would drop significantly.
Head pressure for the compressor will go up, not down.
To Electric Light, I'm not completely disagreeing with your "duty of care" argument.
However, losing a fan unit is something that can happen easily, for many different reasons - the most likely being a fan belt tear. That is essentially what we simulated by turning off power for 6 hours.
I'm trying to determine if the liklihood of something like this repeating itself is high enough that I should include some type of interlock in my future electrical designs for split-systems. This particular system was existing and not my design. If we are going to accept some blame here, I want to make damn sure that the same thing doesn't happen again and if I need to interlock the equipment I will.
Yes, our work initiated the event that caused damage to this equipment, but my point is that it should not have caused any damage at all and if it could have, then the manufacturer needed to include this information somewhere on the unit or in the literature.
If you were at fault, why would the manufacturer replace the unit under warranty? Clearly they thought the unit malfunction was not a result of operating conditions beyond for which it was designed. But I guess it is also possible that they didn't have the full information?
Well in spite of some of the others opinions, heres mine for what its worth:
No way would I accept what they told you, this whole thing sounds like a scam, because the compressor would have not been replaced by the manufacture if there wasn't a problem with the system. kind of like being hit by a driver and it was their fault, but saying you have to pay for the labor, but they will pay for the parts:roll: does this even sound right??? and 10k for labor and gas to replace a compressor??? kind of high if you think about it.
Manufacturers will usually replace the first compressor failure without looking into the cause. If there is more than one failure then they will start asking questions. If the motor winding burned the entire system was probably contaminated with acid. To flush out a system to remove the acid is expensive. Filters to remove any remaining acid would need to be installed.
As for an interlock connecting the two systems there is one. It is called a thermostat. Switching the thermostat from cool to off would have shut off the compressor.
Did the OP cause the unit to fail? In my opinion yes.Weather or not the OP is responsible is for others to decide.
Nope, loosing the evaporator fans will cause a low pressure condition in the return line to the compressor, this should open the low pressure switch.
Loosing the condenser fan will cause the head pressure to go up, this should open the high pressure limit switch.
Yup, I got it backwards. HUA syndrome.
IMO this failure was a co-incidence. As others have said cutting power on air handler normally shuts entire unit down. If it was only 3 years old it had the appropriate controls to shut it down on low and or high pressure. If it continued to run it is more likely original install error.