nec code on wires in 2'' ridge

Status
Not open for further replies.

tcsperson

Member
Can 3 #2, 1 #6, 4 #4, be ran in 30ft of 2'' ridge pipe( burried )? and where in the nec code would help break it down, I've been looking in 310.60 section. I thought that in 2 inch ridge you could run 8 # 2 wires.


Thanks for any help!
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Go to chapter 9, use the applicable tables for the particular conductor types and raceway then do the math.

BTW, welcome to the forums.

Roger
 
il take a crack at it...

assuming thwn-2
3# 2awg .1158 x 3 = .3474
1# 6awg .0507 x 1 = .0507
4# 4awg .0824 x 4 = .3296
+____
.7277
plus grounds...

2" rigid excepts a total 1.363

I say party on!

But im a noob so dont go beting the farm on me. :D
and its 11 2awg thwn-2 in 2" rigid

I am very prepared for some criticism on which steps i might of missed here so let me have it boys...:-?
 