LocalNowhere
Member
- Location
- So. Cal
Here is the breakdown: A new 400Amp service on a house. Feeding a 200 amp sub-panel via a 22k main breaker. Utility Fault Current= 22k. Utility transformer is about 300' away. The inspector is wanting me to use 22k breakers in the sub panel. I did the available fault current calculations and it is nowhere near even 10k. Am I missing something??? I am aware of 240.86, 110.10 etc.
Additional info: Meter panel (400 amp) and sub panel (200 amp) are different manufacturers. And I didn't have Anything to do with deciding or recommending a 400 amp service. I inherited this job from another contractor who had to drop it half way thru.