How close can a receptalce be to a gasoline pump acording to NEC codes?
robert pitre Member Location Houma,la Oct 3, 2010 #1 How close can a receptalce be to a gasoline pump acording to NEC codes?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 3, 2010 #2 robert pitre said: How close can a receptalce be to a gasoline pump acording to NEC codes? Click to expand... There is no restriction in the NEC. The only issue is that if the receptacle is within the classified area, then it will have to be a receptacle suitable for the classification.