rbparks
Member
- Location
- Indianapolis, Indiana
I have 24VDC 40amp fuses feeding 4 terminal blocks that have 8awg wire, in a Nema4x electrical panel. The general forman is requesting to use 10awg wire, 4 of them as tap conductors off the terminal blocks to a 40amp rated device 90-100 feet away. I think it violates the tap rules because the device is rated at 40amps, even though the device only has 10awg terminal blocks, thus the formans request. Does 24VDC follow the same tap rules as 120v 240v 480v, and what are my options? The device is just powering small amperage devices that total up to about 15 amps, but the manufacturer won't come off 40amps for some reason.