Hello gang, I Haven't been here in a while... been busy relocating from FL back to PA!
This is a new one! I got a call from a fellow electrician asking me for a little advice on doing a solar pv system... he has run into a problem with the 120% rule for backfeeding... 200 amp service and 60 amps of inverters... I suggested replacing the 200 amp Mainbreaker with a 175 or 150 if the load calcs permit it. (To avoid a line side connection) He said he already suggested that to the inspector & he said NO because "the panel is rated for 200 Amps, Nothing less"!?!?!?
I said WHAT? I suggested contacting Square D for a list of Main Breakers that were listed for that panel.
I've never heard of a "Minimum" ampacity rating for a Main Breaker... and I doubt it exists... any comments?
This is a new one! I got a call from a fellow electrician asking me for a little advice on doing a solar pv system... he has run into a problem with the 120% rule for backfeeding... 200 amp service and 60 amps of inverters... I suggested replacing the 200 amp Mainbreaker with a 175 or 150 if the load calcs permit it. (To avoid a line side connection) He said he already suggested that to the inspector & he said NO because "the panel is rated for 200 Amps, Nothing less"!?!?!?