I'm wondering what the temp rating of the lugs might be.....
I'm not back to work for a couple days, so I'm going on memory.
This Disconnect (interior) has been changed out before due to heat fatigue and I'm told that it is now about 5 years old.
I think it was Challenger, not positive, can check again when I get back there.
I looked on the inside label for lug ratings and didn't find them, I was thinking they might be 60c lugs, has that changed in the last few years , could they be 75 or even 90c lugs ?
100 amp 480 3phase disc, the load is a commercial dishwasher.
4 Thhn line, loaded at about 70 amps each phase.
Temp readings at line side terminals were 100F,80F,80F A,B,C phases,
the load side is about 70F each phase.
Problem:
Personnel reports elect smell.
Wire is discolored near terminal connections (line side only).
______________
The connections are extremely tight but may have built up corrosion.
My thoughts are that we may need to pull in larger wire to accommodate the 70 amp load, as the wire is undersized if the lugs are rated 60 c .
I'm also thinking as a temporary fix , clean terminals might be in order.
Suggestions appreciated.
I'm not back to work for a couple days, so I'm going on memory.
This Disconnect (interior) has been changed out before due to heat fatigue and I'm told that it is now about 5 years old.
I think it was Challenger, not positive, can check again when I get back there.
I looked on the inside label for lug ratings and didn't find them, I was thinking they might be 60c lugs, has that changed in the last few years , could they be 75 or even 90c lugs ?
100 amp 480 3phase disc, the load is a commercial dishwasher.
4 Thhn line, loaded at about 70 amps each phase.
Temp readings at line side terminals were 100F,80F,80F A,B,C phases,
the load side is about 70F each phase.
Problem:
Personnel reports elect smell.
Wire is discolored near terminal connections (line side only).
______________
The connections are extremely tight but may have built up corrosion.
My thoughts are that we may need to pull in larger wire to accommodate the 70 amp load, as the wire is undersized if the lugs are rated 60 c .
I'm also thinking as a temporary fix , clean terminals might be in order.
Suggestions appreciated.