It's not 'too broad', but it sounds like a homework question.
We prefer you do your own homework, and we'll be happy to help you, but not just give you the answer.
Overall (Residential, Commercial, and Industrial):
Service conductors are sized based on the connected load and additionally derated by a diversity factor? True or False
It appears to be too broad of a question..
Service conductors are not to be sized base on the total connected KVA load of an electrical system(load as defined by the NEC). However, they shall be sized base on a derating and diversify factor as mandated by the NEC rule.
It is not a homework question. It is a twofold question.......I graduated from school 12 years ago. You may review previous posts....:roll:
You might not want to review my Posts, But I will confess, I'm still hungry...:grin:
If you want to go to the year of 57' this was the peak of the Baby Boomers... Boo YA...
Well, my respects to you. How about you share some of your knowledge to bring me up to your standards..
"Diversity" appears 6 times in the 2008 NEC.
Table 310.15(B)(2)(a) FPN.
400.5(B) FPN.
Table 520.44.
Annex B (3 times).