This clears up some of the things that I was wondering, I kind of felt you were not here in the States, not that it make a difference, but with what the local laws and regulation you might be under compares to what is required here, knowing this helps us to apply what is required better.
I think I can best describe your system as a grounded delta, not at all uncommon for other country's, it is basically a 3-phase delta with a corner ground, we also use in some industrial plants a corner grounded delta system, and the "B" phase is the one we are required to ground, now this same system is also used when a ungrounded delta is requested but in this case "B" phase would not be grounded.
If we do install an ungrounded system the NEC does require a ground monitor alarm system to warn of a grounded phase, as we know it wont open a breaker till the second phase is grounded, this is to allow continued operation till a safe shut down can be scheduled, this is one of the reasons some larger company's will request an ungrounded system.
Again these are only allowed where the installation meets the requirements of 250.21