dhalleron
- Louisville, KY
Sorry so long. I've been through this before, but I need another reminder.
I looked at a job today that needed a panel replaced. Seemed like a simple job until I looked closer.
I need to get a permit for this and want to make sure it is correct. I haven't asked the inspector what he will allow yet.
Two buildings 50 feet apart under same ownership.
First building:
Has the existing service probably 30 years or more old with a trough feeding 5 meters with fusible 100 amp disconnects under them. Driven ground and water ground are here.
4 EMT conduits from disconnects into the dirt feeding 4 main lug only panels in remote apartment building. Who knows what conduit is run under the parking lot. Probably rusted out EMT.
Remote apartment building:
EMT conduit in the wall and probably coming out of the slab to main lug only panel.
Remote building has no driven ground or water ground.
Panel has 3 #2 AWG conductors only. No ground except for what it might get from the conduit. The branch circuit grounds and neutrals are under the same bar. The feed #2 neutral conductor was marked green by somebody.
This remote building has a total of 4 apartments with panels wired the same way.
If I replace this panel, can I just bond the neutral to the panel and put the grounds on the same bar? Is there a need for a driven or water ground?
No telling what code this was installed under and was it ever correct? I?m looking at Article 250 of 2005 NEC. The metal conduit underground seems to be the thing that might make me need to install a grounding electrode at the remote building.
Any other thoughts on this?
Thanks.
First building: