doslover

Member
Location
Oregon
Occupation
Retired Journeyman Electrician,
I have just installed a 10kv generator for a customer. Grounded the generator with a new separate # 4 copper to the existing utility ground rods. Inspector says No!
Could not find where he is right or wrong. Do not want him on my bad side. Comments ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Does the transfer switch actually switch the neutral or not ?
(This will effect the grounding means.)

In general, you are probably in violation of 300.3(B)
 

doslover

Member
Location
Oregon
Occupation
Retired Journeyman Electrician,
Grounding a generator

Does the transfer switch actually switch the neutral or not ?
(This will effect the grounding means.)

In general, you are probably in violation of 300.3(B)


Neutral does not switch.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the neutral is not switched then, IMHO, the generator needs a Equipment grounding conductor and, as mentioned, 300.3(B) would require that to be run with your circuit conductors.
 

doslover

Member
Location
Oregon
Occupation
Retired Journeyman Electrician,
If the neutral is not switched then, IMHO, the generator needs a Equipment grounding conductor and, as mentioned, 300.3(B) would require that to be run with your circuit conductors.

Have a #8 ground wire from transfer switch to ground lug in generator control panel. The
# 4 copper is from the external ground lug to rods.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In that case, I don't see a problem.....
did the inspector give you a Code reference ?

(shot in the dark.. if the generator neutral bonded to the frame ?)
 
Last edited:

ceb58

Senior Member
Location
Raeford, NC
Thanks for the feedback. Sort of the direction I was thinking.
I'll see if i can get the inspector to reconsider.

Regards.

After rereading the post I think you have violated 300.3 B. Since you have an EGC ran with the phase conductors you are good. But you have ran another EGC outside the phase conductors to the utility rods. Had you just driven another rod at the gen and bonded it with your EGC in the gen. then it would have been OK. Supplemental rod. You may also want to check the install instructions as most state to drive a rod at the gen.

(shot in the dark.. if the generator neutral bonded to the frame ?)

That is something you need to verify. In this install there is no connection between the neutral and ground.
 

tom baker

First Chief Moderator
Staff member
250.32 does not apply to generators (optional Standby - which is like 90% of all generator installations).....

The reason for grounding generators is based on installation instructions from the manufacturer.
And, some generator mfgs take the easy way and require ground rods, because AHJs and electricians don't understand the rules. By some I mean Siemens and Generac. I went to a seminar and they said we require ground rods regardless of the what the NEC requires. Cummins has a good set of drawings that clearly shows a single point ground.
What our AHJs state is if the mfg requires ground rods, then we require ground rods.
 

ceb58

Senior Member
Location
Raeford, NC
But have we answered the orignal question?

Have a #8 ground wire from transfer switch to ground lug in generator control panel. The
# 4 copper is from the external ground lug to rods.

Grounded the generator with a new separate # 4 copper to the existing utility ground rods. Inspector says No!
 

doslover

Member
Location
Oregon
Occupation
Retired Journeyman Electrician,
But have we answered the orignal question?

Thank you ceb58

The generator manufacturer says to ground the unit with ground rods.

There neutral and ground are not connected.

I have a # 8 wire running with the generator circuit.

I have installed a # 4 wire from the generator housing lug to the ground rods used by the utility.

Can I share the ground rods ??
 

ceb58

Senior Member
Location
Raeford, NC
Thank you ceb58

The generator manufacturer says to ground the unit with ground rods.

There neutral and ground are not connected.

I have a # 8 wire running with the generator circuit.

I have installed a # 4 wire from the generator housing lug to the ground rods used by the utility.

Can I share the ground rods ??

I will say no. The mfg. instructions tell you to drive a rod then drive a rod and tie it to the lug. Get rid of the #4 from gen. to utility rods and keep the #8.

250.32 does not apply to generators (optional Standby - which is like 90% of all generator installations).....

The reason for grounding generators is based on installation instructions from the manufacturer.
Pierre's comment is correct. Code wise you are not requried to drive a rod at the gen. but most mfg. instructions state a rod is requried so not driving one violates 110.3 B.
 