I am studying for the Washington State Electrical Administrator Exam. I am confused about how to determine a branch circuit for a garage door opener.
Using article 430 of the NEC it appears to me that the amperage would be 9.8 amps (for a 1/2 hp motor) and the multiplier for the branch circuit short-circuit and fault-interrupter would be 2.5 for the inverse time breaker. That gives 24.5 amps that leads to 25 or 30 amp breaker. However, I am told that the breaker would only need to be 15 amps based on Article 220.
Can someone clarify this for me? Thanks so much. Dave
Using article 430 of the NEC it appears to me that the amperage would be 9.8 amps (for a 1/2 hp motor) and the multiplier for the branch circuit short-circuit and fault-interrupter would be 2.5 for the inverse time breaker. That gives 24.5 amps that leads to 25 or 30 amp breaker. However, I am told that the breaker would only need to be 15 amps based on Article 220.