Hypothetical: I have a 480/277 service. The service feeds two transformers that output 120/208.
How many systems are present?
How many systems are present?
but of course this is also my opinion of what should be the definition of a SDS also, not the one we now have.
(C) Ungrounded Conductors. Where the premises wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a branch circuit shall be identified by phase or line and system at all termination, connection, and splice points. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means. The method utilized for conductors originating within each branch-circuit panelboard or similar branch-circuit distribution equipment shall be documented in a manner that is readily available or shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment.
How close are they? Or is this a hypothetical installation?
Hypothetical. I think Don's logic is sound - but I think it could be written clearer.
Let's say there's 3 systems.
What means of identification do you use for the two 120/208v systems?
Hypothetical: I have a 480/277 service. The service feeds two transformers that output 120/208.
How many systems are present?
There are three systems, but for the purpose of 210.5(C) there are only two systems as there are only two "nominal voltage systems".
210.5(C) Ungrounded Conductors. Where the premises wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a branch circuit shall be identified by phase or line and system at all termination, connection, and splice points. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means. The method utilized for conductors originating within each branch-circuit panelboard or similar branch-circuit distribution equipment shall be documented in a manner that is readily available or shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment.
210.5(C) Ungrounded Conductors. Where the premises wiring system has branch circuits supplied from more than one nominal voltage system of a different voltage, each ungrounded conductor of a branch circuit shall be identified by phase or line and system at all termination, connection, and splice points. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means. The method utilized for conductors originating within each branch-circuit panelboard or similar branch-circuit distribution equipment shall be documented in a manner that is readily available or shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment.
Yes, mixing the systems of the same nominal voltage would be a problem, but where do you draw the line on this? A large building could easily have 20 or more systems.What would be the problem with the above code in the case of having two derived 480/277-208/120 systems in the same building?
I can see one major one, if both gets marked with the same identification. ...
No direct electrical connection, whats wrong with that def?
Separately Derived System. A premises wiring system whose power is derived from a battery, from a solar photovoltaic system, or from a generator, transformer, or converter windings, and that has no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.
Yes, mixing the systems of the same nominal voltage would be a problem, but where do you draw the line on this? A large building could easily have 20 or more systems.