On a three story house, has second and third floor balconies, walk area on decks are waterproofed and underneath ceilings are closed. Have wiring for lights and fans in ceiling. Inspector saying that the wiring has to be UF cable because it is in damp location. Is this true? What code is it? Another question same scenario, open ceiling do we have to run UF? Another question sleeves for wiring residential center island and floor receptacle inspector says cannot run Romex and conduit due to condensation. Any help would be appreciated.
Does this apply to your installation?
From:
http://www.ecmag.com/?fa=article&articleID=8918
" Running Type NM-B cable outdoors is apparently still a question in the minds of many installers.
If NM cable is run under the shelter of a patio roof or in an overhang where it?s not subject to mechanical damage and not out in the weather, then it should be fine, right? Also, if the NM cable is run in a metal conduit outdoors and isn?t subject to the weather, what would be wrong with that?
Hey man, are you asking or telling? NEC 334.12(B)(4) is very clear. Type NM cable shall not be used in wet or damp locations. Under a patio roof or in an overhang is a damp location. Before you consider running NM cable in a metal conduit, check the raceway articles under 342.22, 344.22 and 358.22. They all say, ?Cables shall be permitted to be installed where such use is not prohibited by the cable article.? Type NM cable cannot be run in any raceway, other than using the raceway as a sleeve for protection in accordance with 334.15(B) and 300.154(C)."
As to the island I agree with him.