Is the statement below in Red a fact ?
We did a new service and transformer installation for a small restaurant. Power company could not give us the required 200 Amp 120/208 power that was needed in a timely manner. Only 227/480 was available.
We installed a 200 amp 600 volt meter socket (provided by the power company) below the meter socket a 100 amp 600 volt locking fused switch, then into the basement with # 2 THHN feeders to the 75 KVA transformer.
Out of the transformer and directly up to the first floor (About 10' - 14') to a 200 amp main breaker panel.
Job is done, but the prints had to be re done to show the higher voltage and transformer.
The engineer sent the prints out showing a load side 200 amp disconnect on the transformer. When we questioned it .. the notes in Red are their answer Via E-mail
NEC REQUIRES secondary disconnect for conductor protection on the load
side of the transformer with-in 10' and in line of site of the transformer.
Breaker in the panel CAN NOT serve as the disconnect.
Maybe we are missing something .. but we thought a line side disconnect would be required .. not one on the load side
Any help would be appreciated .. to add a 200 amp switch to the load side now would be a nightmare
We did a new service and transformer installation for a small restaurant. Power company could not give us the required 200 Amp 120/208 power that was needed in a timely manner. Only 227/480 was available.
We installed a 200 amp 600 volt meter socket (provided by the power company) below the meter socket a 100 amp 600 volt locking fused switch, then into the basement with # 2 THHN feeders to the 75 KVA transformer.
Out of the transformer and directly up to the first floor (About 10' - 14') to a 200 amp main breaker panel.
Job is done, but the prints had to be re done to show the higher voltage and transformer.
The engineer sent the prints out showing a load side 200 amp disconnect on the transformer. When we questioned it .. the notes in Red are their answer Via E-mail
NEC REQUIRES secondary disconnect for conductor protection on the load
side of the transformer with-in 10' and in line of site of the transformer.
Breaker in the panel CAN NOT serve as the disconnect.
Maybe we are missing something .. but we thought a line side disconnect would be required .. not one on the load side
Any help would be appreciated .. to add a 200 amp switch to the load side now would be a nightmare