MDP Bus for splice

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Isn't that where it terminates anyhow. I don't see a code issue with it.
 
Are you drilling and tapping the bus? The manufacturer may not permit such an exercise. Call them or email them and ask if they permit it. If they do, ask for an email conformation. It is always good to get it in writing for future issues.
 

pitkas

Member
Location
Alaska
I am installing an ATS, and I need to break the neutral. The problem is the feeders come out of the ground (via conduit) then go behind the bus with six other feeders and land on the breaker. I can not trace the neutral and I am not going to guess so I see two open spaces where I can land the incoming and outgoing neutral.
 