I am attempting to add amperage to an existing 120/240V service which has #1 THHN feeding a 200A rated meter in a 200A rated meter box with a 100A disconnect below. My question is: What is the trade and/or common name of the 100A feed through breaker below the meter? I am attempting to upgrade to 150A into the building as per the amperage rating of the existing conductors. Thank you for time.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
First what type of building? If not a dwelling you #1 AWG conductors might be too small if your load exceeds 130 amps. Also, if they're in a wet location they need to be THWN or some other wet location conductor. If the existing 100 main is in a separate 100 amp enclosure that will need to be replaced as well. Basically it's called a 3R enclosure with a main breaker, suitable for use as service equipment.
 