Is there a size limit for trapeze mounting a step-down transformer, 480-->208 3 phase? I know above 50KVA it has to be in a ventilated space etc. Right now we have a 225kVA transformer with little space, trapeze mounting it above the panels (in a air conditioned space) would be a perfect solution.

Thanks in advance.
 

iwire

Moderator
Staff member
Location
Massachusetts
Electrically no problem, mechanically, structurally maybe.

I have hung 300 KVA trans before but I had engineered drawings showing the building structure could handle it and that the trapeze was strong enough.

This is not a load you want to hang from the bottom chord of a standard metal truss.

We had specific instructions how to hang it from the tops of I-Beams with 3/4" threaded rod.
 

Mike01

Senior Member
Location
MidWest
When space is limited I always enjoy informing the customer that we will be installing their equipment with skyhooks.

I love telling the desigers (architectural) that who always seem to conviently forget that the electrical equpment needs somewhere to "live". I will never forget one time I had a designer tell me "Ok, but can I see the color selection" I laughed they did not so I slowly walked away...
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We always hang them when the space is tight. Here's two small ones with about 8' of clearance under them.