Have the # of RHW conductors allowed in a piece of 1 1/4" EMT changed since the early 1960's? I have a job where 3 #1 RHW conductors are in a piece of existing 1 1/4" EMT.
3 # 1 RHW conductors. .2660 x 3 = .798
1 1/4" EMT 40% fill = .598
Is my math correct?
Rob..... I see no mention of any RHW with or without outer covering.
Go to the asterisk at the end of the table
You must have a different 1962 than I do.
I thought he was asking about todays code but I see he is asking if there is a code change. Obviously there is a discrepancy. :grin:
I was posting from the 1962 since the OP was asking about "early 60's". The with/without outer covering doesn't show up until the '65.
For RHW without outer covering the correct conductor dimension is (.1901). What type of RHW do you have? Was RHW without outer covering even made in the 1960's?
So if his conductors are without he's good. If not, then there's a violation that has lasted 50 almost years. :roll:
So if his conductors are without he's good. If not, then there's a violation that has lasted 50 almost years. :roll:
Even in the 60's the code was ignored by some.