grounding bushing

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
More facts are needed to tell you for sure, but if the disconnect has overcurrent protection and the system is <250 volts to ground, probably not.
You need to review 250.92(B), 250.96. 250.97, & 250.98 to see if any of those situations exist.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Like Augie stated there is no direct answer given the information provided. One would need to know if this is a service raceway (not likely given your description), the voltage, and the type of KO's being used.
 