sharing a neutral in heath care

Status
Not open for further replies.

Jodonnell

Member
I am working in a outpatient surgical center. The original installation they are sharing neutrals on like circuits thought the entire installation. Is this a code violation since it is in health care? I have not been able to find anything in the code book.....
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
It has always been a common installation practice in health care facillities however, when the 2011 goes into effect in your area, MWBC's will not be permitted in Patient Bed locations.

Roger
 

MNWildcat

Member
Location
MN
With the newer handle tie requirement for MWBCs, our office has changed to separate neutrals for each circuit. So a 3-circuit HR would have 3L, 3N, and 1G.
We design a lot of health care facilities, and this is used for all of the occupancy types we work on.
It is better for the owner to not have to turn off three circuits just to perform some maintence/work on one circuit. This would apply to lighting as well since 3-circuit could take out a major portion of a floor just to adjust one room.
It is more copper, but the maintaining flexibilty if worth the extra copper cost.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
With the newer handle tie requirement for MWBCs, our office has changed to separate neutrals for each circuit. So a 3-circuit HR would have 3L, 3N, and 1G.
We design a lot of health care facilities, and this is used for all of the occupancy types we work on.
It is better for the owner to not have to turn off three circuits just to perform some maintence/work on one circuit. This would apply to lighting as well since 3-circuit could take out a major portion of a floor just to adjust one room.
It is more copper, but the maintaining flexibilty if worth the extra copper cost.

It is not only more copper, due to the increase of current carrying conductors it will cause more conduit, boxes, cable assemblies, or what have you to be used.

Roger
 

sii

Senior Member
Location
Nebraska
It is not only more copper, due to the increase of current carrying conductors it will cause more conduit, boxes, cable assemblies, or what have you to be used.

Roger

And labor to install it...sustain the industry!
 

mpd

Senior Member
just did an inspection, and the engineer specified no shared neutrals and would not accept MWBC's, makes sense one circuit could affect other circuits
 