I'm very sorry but I need help. I'm looking in 300 for where I need a fitting here. This is one of three signs involved in today's scope of work. Couldn't find the MC in the soffit so opened the sign to see if they stubbed the cable in. Long story but need to list the violation or violations here.

Thanks.

Moessign.jpg
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
I think I may also have a violation of 330.30(A)(11) as there is no gasket or caulking behind this sign.
 

jumper

Senior Member
No mc connector

Yes

300.10 Electrical Continuity of Metal Raceways and
Enclosures. Metal raceways, cable armor, and other metal
enclosures for conductors shall be metallically joined together
into a continuous electrical conductor and shall be
connected to all boxes, fittings, and cabinets so as to provide
effective electrical continuity. Unless specifically permitted
elsewhere in this Code, raceways and cable assemblies
shall be mechanically secured to boxes, fittings,
cabinets, and other enclosures.


330.40 Boxes and Fittings. Fittings used for connecting
Type MC cable to boxes, cabinets, or other equipment shall
be listed and identified for such use.

no red head:-?

No

IIRC, not required.
 
Last edited by a moderator:

LEO2854

Esteemed Member
Location
Ma
Yes

300.10 Electrical Continuity of Metal Raceways and
Enclosures. Metal raceways, cable armor, and other metal
enclosures for conductors shall be metallically joined together
into a continuous electrical conductor and shall be
connected to all boxes, fittings, and cabinets so as to provide
effective electrical continuity. Unless specifically permitted
elsewhere in this Code, raceways and cable assemblies
shall be mechanically secured to boxes, fittings,
cabinets, and other enclosures.


330.40 Boxes and Fittings. Fittings used for connecting
Type MC cable to boxes, cabinets, or other equipment shall
be listed and identified for such use.

no red head:-?
No

IIRC, not required.

Yes i know about no red heads on MC cable but we use them anyway:)

What is IIRC :confused:
 
Last edited by a moderator:

Jim W in Tampa

Senior Member
Location
Tampa Florida
Not yet, he hasn't got his inspection yet. I was only able to wire one of 3 today. Fortunately the restaurant owners are both ex construction PM's and are on my side here.

Take pictures for the inspector. Call the sign company and thank them for sending his 8 year old son but kindly send an electrician. If he is this stupid he needs go back to flipping burgers
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Take pictures for the inspector. Call the sign company and thank them for sending his 8 year old son but kindly send an electrician. If he is this stupid he needs go back to flipping burgers
I spoke to them on the phone today but I won't get into how bizarre that was. The installers super is supposed to call me Monday.
 
Location
So Flo
You never know what you will find when you open a sign face, spiders, lizards, bugs; but the wiring violations seem to be a given.:grin: Are those LED's?
Haven't seen one like that yet.
 