I?m looking for reference information about how to include electrical testing (low voltage) in my estimate or bid documents? Is there any recomended % based on man-hours ?
Regards
Nef
Regards
Nef
He is talking low voltage jobs.
Yup more information on what type of workLow Voltage is defined as <1000V. So how are we supposed to have any idea what he means.
Regards
Nef
If the specs call for "Independent Testing or Third Party Testing", it means just that.
You need to send the plans and specs to a NETA Certified testing agency to get a quote as a subcontract to you for this work.
Sometimes there is a complete, spec section for this that is very descriptive of all systems required.
Sometimes each section of the specs describe the testing for that section, such as, grounding, feeders, conductors, generators/xfer swithes, devices. A lot of the testing required for switchgear, such as arc flash, selective coordination studies, GFI and such, will be by the manufacturer.
Don't take this lightly or try to price it to perform yourself, if that's not what they are asking for.
I've had testing subs run from $14K to $100K. There is no magic percentage or sq/ft number to cover this.