power company meter reads in kw if you have a 120 volt 1500 watt heater @12.5 amps and a 240 volt 1500 watt heater @6.25 amps will the power company meter read the same for both heaters because both are 1500 watts?
Not sure what you mean by "cycle rate". Are you thinking that a 240V 1500W heater comes on less often than a 120V 1500W heater to heat up the same amount of room air space? If so, it's still irrelevant. Heater watts relate directly to BTUs of heat into the space. On and off time relates to the thermostat being satisfied, which is going to be based on BTUs. it's all the same.Sorta, watts are watts, but the meter reads kwh and the cycle rate is a factor.
If using a 2-current, single-voltage meter to read single-phase loads (what is mostly used):Yes, The 1500 w 120v Plus 1500 w 240v = 3 kw If on for 1 Hr. steady you will be billed 3 kwh