25 ohms

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
Is their anyware in USA that you can 25 ohms or lower on a 8' ground rod driven in earth?
 

skeshesh

Senior Member
Location
Los Angeles, Ca
Is THERE ANYWHERE in [the] USA where one can measure 25 Ohms or lower on a 8' ground rod driven in earth?
(sorry could not resist)

I wonder, what is the difference if you find someone who has achieved that rating? Bottom line is, if you are a proper contractor, you should have the means to measure the rod's resistance really easily. Once you do, if you do not achieve the criteria, then you have to drive another rod to do so. Alternatively you can just drive more than one in any case.
I'm not trying to discredit your question as a fun fact to know, but I doubt it has any practical outcome on any installation you may do or encounter.
 
Last edited:

broadgage

Senior Member
Location
London, England
I have certainly achieved less than 25 ohms here in the uk from a single ground rod.
Readily achieved in damp or marshy land, but unlikely to be achieved in dryer conditions.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I wonder, what is the difference if you find someone who has achieved that rating? Bottom line is, if you are a proper contractor, you should have the means to measure the rod's resistance really easily. Once you do, if you do not achieve the criteria, then you have to drive another rod to do so. Alternatively you can just drive more than one in any case.
I'm not trying to discredit your question as a fun fact to know, but I doubt it has any practical outcome on any installation you may do or encounter.

I would bet that most contractors do not have the equipment to measure the resistance of one rod nor do they care to.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Is their anyware in USA that you can 25 ohms or lower on a 8' ground rod driven in earth?

Frankly, unless you have a soils report where resistivity measurements were done, and an engineer to do the grounding design, I would assume you will not achieve 25 ohms or less with one rod, and make sure you put 2 rods and associated hardware and labor in your bid, and be done with it.
 

zog

Senior Member
Location
Charlotte, NC
I posted a series of maps showing soil resistivity a while back but can't seem to find that thread. But in swampy areas or areas where the soil is very fertile you may be able to acheive 25 ohms. But as others mentioned, 99% of EC's do not have the equipment to test it anyways so it is just easier to drive a 2nd rod.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
101208-1118 EST

In my yard and at the shop I have less than 25 ohms. From memory in the 10 to 20 ohm range. This is a clay loam soil and generally there is moderate moisture present below a few inches.

In our part of the country we have green foliage as compared to somewhere like Colorado.

.
 

zog

Senior Member
Location
Charlotte, NC
101208-1118 EST

In my yard and at the shop I have less than 25 ohms. From memory in the 10 to 20 ohm range. This is a clay loam soil and generally there is moderate moisture present below a few inches.

In our part of the country we have green foliage as compared to somewhere like Colorado.

.

I used to do a ton of ground testing in that area (based in Novi) and I do not recall ever getting <25ohms from single rod. What method are you using for your test?
 

Cavie

Senior Member
Location
SW Florida
In Florida it is easy to get 25 ohm on one rod in the summer rainy season. I do FDOT roadway and signal work. You will drive as many rods as needed to acheive 25 ohms on lighting and 15 on many signal projects. I have a clamp on ground rod tester. looks just like a standard amp probe only bigger. I am in a fight with an inspector on the east coast that is telling me I need 3 POINT TESTER and I must check every one of the 196 rods on the project one at time. The directions for my tester tells me to hook up a complete grounding system and check it once at the service point. Eliminating the need for individule testing. The inspectors boss says I can follow the directions on my tester. The inspector and his boss are discusing the matter. I let you know the outcome.
 

iwire

Moderator
Staff member
Location
Massachusetts
The clamp tester is almost junk IMO.

Unless the test is done perfectly it is mealiness.

Zog has posted many times about the clamp meters short comings.
 

Cavie

Senior Member
Location
SW Florida
The clamp tester is almost junk IMO.

Unless the test is done perfectly it is mealiness.

Zog has posted many times about the clamp meters short comings.


Shusssh. Don't let the inspector hear you say that. I believe that one 20' copper ground at each pole is enough. They are all connected together with a #6. All 196 of them
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I believe that one 20' copper ground at each pole is enough. They are all connected together with a #6. All 196 of them

I agree with you Cavie and to go one step further, (I know it won't help in your battle) it wouldn't matter if they measured in the hundreds or even thousands of ohm's as far as performing their intended job.

Roger
 

480sparky

Senior Member
Location
Iowegia
I can drive a whoooooooole lotta ground rods for the cost of the proper test equipment and the labor to conduct the test.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I can drive a whoooooooole lotta ground rods for the cost of the proper test equipment and the labor to conduct the test.

And in most cases, especially residential and small commercial projects, that will suffice but, on projects that have specific GES performance specs the tests must be done, and if the permitting process of the particular area includes plan review it can become part of the inpectors requirement for the final.

BTW, we just drive two rods too if we are not required to test :)

Roger
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
101208-1749 EST

ZOG:

One test was done between So. Industrial and the Ann Arbor Railroad tracks midway between Stadium and Eisenhower. The tracks follow what was once a creek bed.

I used a source and sink, each was an 8 ft rod, with a spacing of about 40 ft. There is virtually no ground path current here, millivolts, maybe 100 MV. Thus, a negligible error from ground path 60 Hz currents, or any other frequency. Excitation was 60 Hz from a Stancor 28 V 2 A transformer. Then used Fluke 27 to essentially do a fall of potential test. No frequency filtering on the input to the Fluke.

I do not know where to find the experimental data at the present time. This test was a number of years ago.

If I ran this test in Dearborn where there is some very sandy soil I would never get this low a reading. But it also means you do not get water in your basement.

.
 

brian john

Senior Member
Location
Leesburg, VA
And in most cases, especially residential and small commercial projects, that will suffice but, on projects that have specific GES performance specs the tests must be done, and if the permitting process of the particular area includes plan review it can become part of the inpectors requirement for the final.

Roger

And I make money doing this, SO TEST AWAY PLEASE!!!!
 

glene77is

Senior Member
Location
Memphis, TN
101208-1118 EST
In my yard and at the shop I have less than 25 ohms. From memory in the 10 to 20 ohm range. This is a clay loam soil and generally there is moderate moisture present below a few inches.
.

Gar,
In Memphis, TN, I have asked the code enforcement office about GEC requirements in situations where the residential plumbing is all plastic.
They say, "If the plumbing is plastic, then there is nothing to attach to", and
the inspectors do not require a second ground rod (as required by NEC).
So, we have just let the inspectors determine what is sufficient.
When in doubt, ask the AHJ.
 