Using different brands of strut together

Status
Not open for further replies.
It is formulated in my original response. I just wanted to throw it by the forums to be sure I'm not missing something. Phew, I'm not crazy.:D
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
If he's trying to call you on listed strut:roll: I'm almost scared to ask how the rest of the inspection went?
 

RyanA

Member
Location
Wyoming
110.3 (B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.

What do the instructions for the strut say? I honestly can't say that I've ever seen instruction for strut.
 

kwired

Electron manager
Location
NE Nebraska
I suppose you are not allowed to use one brand of clamps in another brand of channel.

Better not hang raceways from lumber cut at different mills either.

You also cannot use more than one brand of raceway or fittings on any individual project

All conductors must be from same manufacturer.

P&S receptacle can not have a Leviton wall plate installed on it.

If service equipment is Square D you can not use Siemens safety switches or motor controls.

I can come up with many other items that must come from same manufacturer.

You also can't dig a trench with a Ditch Witch and backfill with a John Deere.
 