695.6(E) Pump Wiring. All wiring from the controllers to the pump motors shall be in rigid metal conduit, intermediate metal conduit, liquidtight flexible metal conduit, or liquidtight flexible nonmetallic conduit Type LFNC-B, listed Type MC cable with an impervious covering, or Type MI cable.
The jockey pump wiring is not required to be wired like a fire pump.
What is a jockey pump
A jockey pump is used to maintain pressure in a system so you don't get false alarms and fire pump starts and stops. At least that is what i have been told.
A jockey pump, or a pressure maintenance pump, is a small apparatus that works in conjunction with a fire pump as part of a fire protection sprinkler system. A jockey pump is designed to keep the pressure elevated in a fire suppression system so that the main fire pump is prevented from running unless absolutely necessary. It consists of a motor, a pump, and a controller.
The fire pump will not cycle once it starts it must be shut down by hand. Just going from the ones I have installed