I have a problem with a peckerhead and was wondering if anyone out there has come acrossed this, and if you have any suggestions
I have a 400hp motor that will be feed with Parallel 4" conduits the peckerhead has only 1 - 4" opening. I thought about setting a pull box and running my 2 conduits to it then bringing one 4" to the peckerhead but then I get into derating becuase the length of flex will not be that short with 4" (by the way the conductors are 350's VFD cable that is why the conduit is so large)
The other problem is that the motor has 4 conductors per phase along with my 2 conductors per phase is a lot of wire in the peckerhead. The factory peckerhead is 15.2"L x 10.2"W x 8.8"D not enough room for the terminations.
What I would like to do is have my fab shop beef up the back of a hoffman type 24x24x12 Nema 4x j-box, (motor is outside) and cut the mounting patteren into the back of that. Then I could use the factor gasket and mount the box directly to the motor, then I would have room to make the terminations.
I have talked to the motor manufactur to see what they suggest but the first person I talked to did not have a problem with my box idea he wanted to run it by the applications eng first.
What are your thoughts.