I have a range in a residential dwelling with a 10.8 kw nameplate rating. The panel is a ITE Pushmatic, the terminal temperature is AL/CU 40 degrees on the circuit breaker. My question is with a 10.8 kw divided by 240v = 45 Amps which is a 50Amp o.c.p.d.Table 220.55 allows me to use Column C at a demand factor of 8; 8000kw divided by 240v =33Amps which allows me a 40Amp o.c.p.d. Using Table 310.16 Tells me that #8 cu thwn gives me a 50 amp capacity or #6 al thwn, and 40Amp capacity for #8 cu at 60 degrees or #6 al at 60 degrees. My confusion lies with the terminal rating of 40 degrees on the ITE circuit breaker, can i use an o.c.p.d. at 40 or 50 Amps?