Good call also. Thanx. I have learned the error of thinking.
I gotta laugh at myself on this post.
Quite funny in a way.
I meant my error of my thinking an EGC as a circuit conductor.
Good call also. Thanx. I have learned the error of thinking.
[/B][/COLOR]
I gotta laugh at myself on this post.
Quite funny in a way.
I meant my error of my thinking an EGC as a circuit conductor.
Now you have learned the error of your typing.
So, it looks like I lose ... thanks for your opinions, everyone!
Jason
Maybe maybe not. I am not totally convinced yet. Under definitions there is nothing for "circuit conductors"
I do find such an install unlikely as why would we cut the ground if pulling all the wires in 1 ?
What i do try to do when practicle is make a small loop in the box for future use.
If there is logic in this that something changes if we cut so much as 1 hot wire that we need bonding but if we cut a grounding wire not then please tell me what it is.
Maybe maybe not. I am not totally convinced yet.
I do find such an install unlikely as why would we cut the ground if pulling all the wires in 1 ?
Regardless of your lack of agreement an EGC is never an NEC circuit conductor, many code sections have been posted proving it.