Do wall spaces behind appliances (fridge, range, DW, etc.) in a dwelling-unit kitchen require a 120v 15- or 20a receptacle per 210-52(A)(2)(1)?
Since you ID'd them as wall space, guess what I said?
Well, gee, they are walls aren't they? We're not talking about the floors and ceilings now!
You should have clarified free standing or built-in.
What's the difference? A wall is a wall is a wall.
This may be part of the reason that we are butting heads.
...Look at fig 210.52(C)(1)
...the wall space behind the counter top ranger is exempt
...the wall space behind the counter top range is exempt
...you say your talking about 'wall space,' than I think you need to explain the exact situation your questioning! Who puts a dishwasher in an 'open wall space' (no counter to left or right, just walls:-?)
define 'appliance garages', also read 210.52c4 than continue with c5
OK; the exact situation is:
You're having your final done. The appliances are two weeks out, and not part of you contract. There's an opening between the cabinets for the DW, but it's not installed. Can the inspector require a receptacle there because it's a 24" wall space?
And I will ask again, in vain hopes that someone will answer:
WHAT DO COUNTERTOPS HAVE TO DO WITH CONSIDERING IT A WALL SPACE REQUIRING A RECEPTACLE?