SER above commercial drop ceiling

Status
Not open for further replies.

shepelec

Senior Member
Location
Palmer, MA
In reading 338.10(4)(A) it reffers you to partII of 334.

I'm reading this as to disallow SER above a commercial drop ceiling.
Am I reading this right or am I missing something??
 

TT009

Member
Yes it is a NM cable, which is not permitted unless, covered with a 15 min. rated finish in a commercial application.
 