Can I use EMT (encased in concrete)for floor boxes encased in concrete?
In slabs above grade yes you can.
In slabs above grade yes you can.
Actually you can use it in direct contact with earth if you meet the requirements of 358.10(B)
Roger
Actually you can use it in direct contact with earth if you meet the requirements of 358.10(B)
Roger
Is galvanized coating not corrosion protection?
"Not in my neighborhood."Is galvanized coating not corrosion protection?
I've seen that on RMC for underground services, but is regular EMT galvanized? I'm not even sure, that's why I asked the question.
Wheatland said:Applications
Wheatland Galvanized Steel Electrical
Metallic Tubing, National Electrical Code?
(NEC?) 2008 Article 358, can be installed
indoors or outdoors, in dry or wet locations,
exposed or concealed, in all kinds of
atmospheric conditions, and in hazardous
locations, when in accordance with the
NEC? and providing it will not be subject
to severe physical damage during and
after installation and is properly protected
against corrosion.