feeder

Status
Not open for further replies.

earlejohnson

Member
Location
ga.
is it permissible to run a feeder through a strip mall inside the building having it pass through multiple rental suites before terminating in a sub-panel.

2008 nec
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Its allowed but you must have a means to disconnect all sources of supply in a building. Go outside or run under slab, or comply with 225.32

I agree, if each tenant space is considered a separate building.

Not all fire rated walls separate a building into 2 separate buildings.

Chris
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
I agree, if each tenant space is considered a separate building.

Not all fire rated walls separate a building into 2 separate buildings.

Chris

Nor would there be a need for fire walls in some cases. Depending on the occupancy group, the level of fire protection changes. If they are group "B" occupancy there may not even be a fire wall separating tenant spaces.
 

defears

Senior Member
Location
NJ
You should talk to the owner and make sure there's nothing prohibiting this in all the leases of the tenants involved. Been biten before. Not fun.:mad:
 
Status
Not open for further replies.
Top