A 45kva dry type transformer was installed inside with an underground conduit feeding the primary.This conduit has no mechanical connection to the enclosure.The vents on the bottom of the transformer have been cut out (with what looks like a shovel)to allow the conduit to enter the enclosure.There is however a bonding bushing with a ground wire attached to the enclosure .I would see this install as a violation of 08-300.10 .The manufacturers spec state that this is an acceptable location to enter this enclosure.I dont see how this vented area will accept the locknuts and create a metallic connection to comply with this code.
Thanks for any input you may have.