What type of insulation does12/2 romex have on the individual wires? same with 12/2 mc? is it thhn?
No it's not, look at another role of NM.romex is thhn and will tell u on conductor..
romex is thhn and will tell u on conductor..
If you read the specifications of most branch circuit MC cable it will state the conductors are type THHN. I have never seen any manufacture state the conductor type in NM cable.
No it's not, look at another role of NM.
Roger
Yes, neccessarily, find us an example of the conductors inside the jacket of NM identified per the requirements of 310.11 and you'll have a valid point, until then the conductors inside the jacket of NM are simply 90 deg conductors that must be used as 60 deg conductors.also not necessarily
Correct.So we don't know what it is.
Never seen it. MC, yes; NM, no.romex is thhn and will tell u on conductor..
Yes, neccessarily, find us an example of the conductors inside the jacket of NM identified per the requirements of 310.11 and you'll have a valid point, until then the conductors inside the jacket of NM are simply 90 deg conductors that must be used as 60 deg conductors.
Correct.
Roger
I await the proof, but I won't hold my breath. Since most companies that make NM also make single conductor types, why would they cut their own throats?I can't say with 100% certainty that there isn't some company out there making a NM-B cable with THHN markings on the wires. Since one person seems to think they saw that, and I found a company that claims they use THHN for the conductors, I have to leave room for the possibility.