Al my exam prep calculations say to take lighting at 125% when it's continuous, as in a commercial building, but I can't find it anywhere in article 220 Load Calculations.
I thought Table 220.12 load minus Table 220.42 Demand Factor was THE minimum lighting load.
The exam prep questions do not ask for:
1) feeder conductor size discussed in 215.2(A)
2) OCPD
3) Servicer
Where loads are taken at 125% when continuous.
What is the code citation I am missing?
I thought Table 220.12 load minus Table 220.42 Demand Factor was THE minimum lighting load.
The exam prep questions do not ask for:
1) feeder conductor size discussed in 215.2(A)
2) OCPD
3) Servicer
Where loads are taken at 125% when continuous.
What is the code citation I am missing?