Softstarters
Cow
Eastern Oregon
I need some help choosing a softstart for a customer. He has a portable grain auger with a 20HP and 7.5HP motor on it. I've installed quite a few drives but never a softstarter yet so I'm pretty unfamiliar with them.
Is it possible to buy one 30HP softstart and add a couple manual motor protectors to protect each of the motors? What about adding a shunt trip bypass contactor to the setup? Or just let the softstarter carry the load full time?
Thanks guys.
Finite10
Great NW
Are you talking about a Primary Resistor Type motor starter?
(I used to own acreage in Christmas Valley, is that near you?)
jim dungar
Wisconsin
PE (Retired) - Power Systems
A soft-starter is basically a variable voltage source. Yes you can feed multiple motors from a single soft-start, but you should not bring a motor on line once the soft-start is in run mode (this is called slamming, and can cause problems just like it does with VFDs).
In general the SCR's of a soft-start will generate losses of about 1.5watt/amp, so a bypass contactor is a good idea.
Cow
Eastern Oregon
Thanks for the replies everyone.
?? I've never heard those terms before....
I live in the Hermiston-Pendleton area, Christmas Valley is a few hours away.
Finite10
Great NW
I've never installed one. It's just in my Industrial Motor Control book, 3rd edition. Here's one for 99 cents.
On page 270 they say this;
They reduce POCO demand, less POCO line disturbance, and lowers your feeder inrush current. It also gives a gradual speed up.
Resistors are in series with motor lead. There's a Vd across the resistor and reduced V to motor. That reduces start speed and I.
As it gets up to sped, the I through the resistor decreases and that decreases the Vd.
E=IR
...and increases V to motor.
At speed, the resistor is cut out of the ckt.
dbuckley
When I was a kid, motor starting meant one of these things:
Yes, all exposed. often with a knife switch there for good measure too...
Hat tip to Wikipedia for the image.