Use the HP rating
Use the HP rating
Does the disconnect you are using have a horsepower rating? For example, there are times when a 30 amp disconnect, which has a 20 HP rating is used in a motor circuit which is protected by a fuse over 30 amps. Case in point, a 20 HP motor with an FLA of 27 amps at 480 volts 3 phase and has a 45 amp fuse in the circuit, yet the "30 amp" switch has a rating of 20 HP.