Spot the Violaions Jan 20 2011

Status
Not open for further replies.

480sparky

Senior Member
Location
Iowegia
Todays' job: Panel swap and clean up some misc. code violations. Here's one:

Outside recep, with a cord plugged in.

DSC_5754.jpg


Notice how the cord wanders & meanders around where people walk.

DSC_5755.jpg


Let's follow it, and see where it goes................

DSC_5756.jpg


Oooh! Not good! Through 2 doors and into the house:

DSC_5757.jpg


Down the stairs....... (I'm sure this ain't very safe, energized or not!):

DSC_5758.jpg


...and across the basement floor..........

DSC_5759.jpg


.............where there's another cord plugged in to it.

DSC_5761.jpg





 

480sparky

Senior Member
Location
Iowegia
Wait a minute! Is that a DRYER cord?

DSC_5762.jpg


By cracky, it sure is!

DSC_5763.jpg


Good, old-fashioned 3-wire dryer recep.

DSC_5764.jpg


Nice box!

DSC_5765.jpg


Needless to say, this got fixed. And the dryer is sure to work better on 240volts than 120!
 

raider1

Senior Member
Staff member
Location
Logan, Utah
There is no handrail on the stairs leading to the basement.;):)

Also the winder configuration of the stairs is too tight and does not have the required 6" minimum tread depth at the shortest point.

Chris
 

jumper

Senior Member
DSC_5759.jpg


Is that dark spot at the bottom a sump pump hole?

SECTION P3007 SUMPS AND EJECTORS

P3007.1 Building subdrains. Building subdrains that cannot be discharged to the sewer by gravity flow shall be discharged into a tightly covered and vented sump from which the liquid shall be lifted and discharged into the building gravity drainage system by automatic pumping equipment or other approved method.
 

stew

Senior Member
I suppose the indoor j box outdoors is just fine as well as no in use cover ,cord as a permanent wirng method,no bush at the last box and box just laying on the floor. Those seem perfectly reasonable probably to the guy that consumed all that alcoholic product eh? Outdoor conduit also looks like water pipe instead of sched 40. Thats the outdoor ones with no straps .
 

paul

Senior Member
Location
Snohomish, WA
It's obvious that this was installed to melt the snow. That's why it's in the walkway! Anyone can see that! Now why they would heat the beer with it, I can't tell you. They should be punished for that. The beer should be outside so that it's nice and frosty cold.
 

PetrosA

Senior Member
It's obvious that this was installed to melt the snow. That's why it's in the walkway! Anyone can see that! Now why they would heat the beer with it, I can't tell you. They should be punished for that. The beer should be outside so that it's nice and frosty cold.

It's not to heat the beer. See all the curlicues in the wire? That's from wrapping it around the cans. Anyone with a basic understanding of thermodynamics knows that Bud Light is best cooled by wicking the warmth away to the outdoors in sub-freezing temperature using copper conductors. Duh.
 