carnes51214
Member
We were called out to a school where a Air handler disconnect had started melting. This is actually the 2nd disconnect that had this problem. Here are the facts. There is #6 wire ran to J-box, then changes to #8 wire thhn to disconnect then down to furnace unit. The furncace unit has 10kva heat strips. The max fuse rating is 60amps. It operates on one leg being 120v and a high leg around 200v. So 240v air handler. I know that #8 is good for 50 amps if using the 75 degree column for the terminals. There were 60 amp fuses in disconnect. Would the smaller wire have caused the fire.
Also when the maintence man pulled out the pull out on disconnect on of the stab blades from pull out was left in the disconnect because it was melted off. So one leg still connecting possibly.
So my question is what could have caused the fire. It was cold that morning around freezing. The first disconnet that had this problem I replaced last year, I just diagonsed the issue as loose terminals. This year it was fine no sign of melting. So what could be the problem. This installation was about 7 years ago.
Also when the maintence man pulled out the pull out on disconnect on of the stab blades from pull out was left in the disconnect because it was melted off. So one leg still connecting possibly.
So my question is what could have caused the fire. It was cold that morning around freezing. The first disconnet that had this problem I replaced last year, I just diagonsed the issue as loose terminals. This year it was fine no sign of melting. So what could be the problem. This installation was about 7 years ago.