I have a customer who wants me to install a 600 amp 3-phase circuit breaker in a NEMA 4 Steel enclosure, for a service.
My question is...
Is this (and any other service MCB/Fuse) supposed to be service rated equipment.
AIC ratings is another question later.
Thanks
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Service Rating

Service Rating

Equipment for a service must be rated "suitable for use as service equipment".
Equipment marked "suitable for use ONLY as service equipment" can only be used as service equipment as the neutral is permantly bonded.
 