tryinghard:
I was having Internet Explorer crash problems this morning. Actually crash of XP as well.
I do not believe in any of my posts that I suggested the neutral be connected to the EGC anywhere except at the one single required location. I used "main panel" to refer to this location. This is a little loose in some situations, but close to the location.
I did discuss that some CNC suppliers have suggested the EGC be disconnected from the machine chassis and this grounding connection be replaced with a local ground rod at the machine. I also said this was a violation and unsafe.
I also indicated that some just added a supplemental ground rod at the machine.
If I take a 100 ft piece of #12 copper wire and make connections at the 20 and 80 ft points to earth, then the existing current in the earth will inject some current into the 60 foot section of the wire.
A normally non-load current wire that is not connected to the required bonding point for an EGC wire is not an EGC. A logical conclusion from the definition of an EGC wire.
With equipment grounding I've never been concerned about looping what-so-ever only effective fault path to/from source. I would think some amount of looping would commonly occur but if so why would this current travel to data equipment?
Looping of the EGC certainly allows current and voltage to be induced in the loop from changing magnetic fields. Further current can be injected into this loop by something like a 12 V battery and 12 ohms resistor, about 1 A. Or many other source types are possible.
Why would current travel to a computer via an EGC?
Assume a common main panel for both the CNC and the computer.
An EGC runs from the main panel to the CNC. There are some noise filter capacitors in the CNC from hot lines to the machine chassis. There is capacitance in the main power transformer and other similar devices from the hot lines to the machine chassis. Maybe there is a little leakage current as well. The low voltage common of all the machine electronics is connected to the machine chassis. Some of these connections to the machine chassis cause noise current to flow into the EGC back to the main panel. Thus, a noise voltage drop on the machine EGC.
Assume no noise is generated on the EGC to the computer resulting from the computer. In reality there likely will be noise generated from the computer thru its EGC also. Next connect the RS232 cable between the computer and CNC. Now a loop is closed, and noise current flows from the CNC thru the RS232 cable to the computer, and back thru the computer EGC wire, and as a result of all of this there is a noise voltage difference between the computer and the CNC.
Fault conditions and lightning cause much worse noise levels.
,