# of neutrals planned?
# of neutrals planned?
Justin, are you intending to use a separate neutral for each dedicated circuit, or are you planning mwbc?
A mwbc 1ph or 3ph would put you in the 50% derating area for 15 amps each, and per T210.21.B.2 you could have max load of 12 amps, which fits your situation.
You couldn't use single pole breakers for your mwbc, if that's acceptable to your client. If not, then as Iwire says, you upsize your wire.
As to marking the recepts with max load, I don't think its required; it's is a nice touch although the time you take to do it eats into your profit margin; but it may be wasted on your client: how many people have a clue how many amps their appliance draws?