GFCI's on 3 phase circuits

Status
Not open for further replies.

hurk27

Senior Member
Just curious, when installing GFCI receps on a three phase circuit, does each phase need it's own neutral, since GFCI's operate due to an imbalance between hot and neutral?

The circuit feeding a GFCI receptacle can be a multi-wire circuit (shared neutral), but not the load side, if you use breakers, single pole GFCI breakers will need their own neutrals, but you can share a neutral with two pole.
 

480sparky

Senior Member
Location
Iowegia
You can feed the GFCI recep with a MWBC, but you can't Line-Load protect any receps beyond the GFCI recep with it.... each circuit must have it's own grounded conductor.
 

normbac

Senior Member
You can feed the GFCI recep with a MWBC, but you can't Line-Load protect any receps beyond the GFCI recep with it.... each circuit must have it's own grounded conductor.

Could you explain that. Are you referring to three phase only. Is wiring a 12-3 to two sa circuits a violation?
 

480sparky

Senior Member
Location
Iowegia
Could you explain that. Are you referring to three phase only. Is wiring a 12-3 to two sa circuits a violation?


A GFCI works by comparing the amount of current on the grounded (neutral) to the current on the ungrounded (hot). If they are more than 5ma different, the GFCI trips.

If you try to use GFCIs on a MWBC to protect 'downstream' receps, one of the GFCIs (or two, in the case of three phase) will trip because the 'hot' and 'neutral' will always be different.

You can feed three GFCI receps with a 3-phase MWBC, but you cannot use the MWBC to protect any 'downstream' receps.... you must use a separate grounded for each circuit.
 

hurk27

Senior Member
Could you explain that. Are you referring to three phase only. Is wiring a 12-3 to two sa circuits a violation?

All he is saying is you can use a MWBC up to a GFCI receptacle but not after it, load side has to have separate neutrals, and yes you can use a MWBC to feed SABC but you now have to have handle ties for the breaker's feeding it.
 

480sparky

Senior Member
Location
Iowegia
All he is saying is you can use a MWBC up to a GFCI receptacle but not after it, load side has to have separate neutrals, and yes you can use a MWBC to feed SABC but you now have to have handle ties for the breaker's feeding it.


Or a two-/three-pole breaker.
 

normbac

Senior Member
So when I see two SA circuits in a kitchen with a 12-3 how is this working are the gfci not protecting correctly. TIA
 

480sparky

Senior Member
Location
Iowegia
This:

2cirgfirecepMWBC.jpg




will not work.



You either need to separate the neutrals after the GFCI receps:

2cirgfirecep.jpg


Or install a 2-pole GFCI breaker:

2cirgfibrker.jpg


Option #2 won't work on three-ph. as I don't think anyone makes a 3-pole GFCI breaker.
 