azezaz123@qwestoffice.net
Does anybody know the formula for calories per centimeter squared , and the explaination of the formula in fairly understandable terms ??
Sunlight falling on the earth's surface comes out to about 1.4 cal/cm^2 , a measure of energy/area, and can take hours to give you a second degree burn.
Arc flash can do the same thing in a fraction of a second.
I think you're right. Sunlight intensity, that is power, is 1 kw/m^2 and I must have scrambled the conversion.1.2 cal/cm2 will give exposed skin a second degree brun in 0.1 second, so I don't think your info is corerect. 1.2 cal/cm2 is the basis of everything arc flash related, arc flash boundaries, ATPV ratings for clothing, etc...
http://www.onlineconversion.com/
A watt is a joule per second and a calorie, with lower case c, is about 4 joules of energy.
To test PPE effectiveness you'd need a really large magnifier.
I believe that that's the strength of sunlight out in space. At the surface of the earth on a clear day at noon it's about 1000W/m^2. It can be a little higher from time to time.The only way you can convert the 'sunlight' example is to assume an exposure duration.
Sunlight intensity is about 1300 W / meter^2 which is 0.13 W/cm^2. Assuming 1 watt = 0.24 cal/s you can conclude the sunlight can deliver about 0.0312 cal/cm^2 every second.
I still don't really understand what the OP was asking though...
There are several different formulas depending on the voltage, equipment configuration, etc.. And there is not a simple way to explain them, in fact the math is more complex than most people can understand.
One if the basic equations is, using the simplified method for LV systems in a cubic box. (I can't even post it right because I don't know how to do subscripts and superscripts in this new format)
EMB = 1038.7DB-1.4738tA[0.0093F2 - 0.0076F + 5.9675]
Where:
EMB = maximum 20 in. cubic box incident energy, cal/cm2
DB = distance from arc electrodes, inches (for distances 18 in. and greater)
tA = arc duration, seconds
F = bolted fault short circuit current, kA (for the range of 16 to 50 kA)
As mentioned, these are not something you should attempt on your own, there are a lot of things to consider and even the pros use high end engineering software to do these.
Was there a specific question you had?
Robert: No I am just trying to understand the calculation for my own information so I can figure out the type of PPE and the boundry distances because I do not always trust a computer to do something I have not understood. Robert
Wow, Robert posted that thread in Feb, and now returns to respond to it. :grin: