I have a 13.2kV to 480Y277V 1000kVA unit substation with a fused main disconnect on the primary side. There is no secondary disconnecting means for the transformer and it is tapped a total of 9 times. I thought you could only tap it 6 times?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
(a) Is this a utility transformer or customer owned ?
(b) Do all the taps terminate in the same area ? same building ?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
How are the taps protected? They must be protected per one of the rules in 240.21(C). The number of taps will be limited to 6 by the rules in Table 450.3(A) unless this is a supervised industrial installation.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
For decades, well into the 90's, it was common practice for industrial unit substations (direct bus connection transformer to feeders) to be supplied with more than 6 devices.

This is still allowed under 240.92(C), although I do not see it being used much on new construction (it definitely is not favorable to arc flash mitigation),
 