richwaskowitz
Senior Member
- Location
- Shelby Twp. MI, near Detroit
I have never seen this before until today. A residence with a 200 amp underground service to a meter, then two 100 amp SEU cables tied together on the load side lugs going into the house to two separate 100 main breaker load centers right next to each other. Both panels have their neutrals and grounds bonded together. Are there violations here other than the fact that the neutral is connected to ground at two different places? Was this a common practice at one time? Installation is about 50 years old.