Can someone help me understand this article, the way it is being explained is that for every "hot" you have to have a neutral, or you can install a three pole breaker, have three hots and one neutral.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
You can use a multipole breaker or listed handle ties.

Roger
 
The engineer is on record is wanting to use breaker ties but the customer engineer says two more neutrals have to be installed so that all three hots has its own neutral. Our local inspector says it refers back to this code but I guess I am not fully understand the code.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The engineer is on record is wanting to use breaker ties but the customer engineer says two more neutrals have to be installed so that all three hots has its own neutral. Our local inspector says it refers back to this code but I guess I am not fully understand the code.

In some situations you may want individual neutrals but the code clearly allows a neutral for a multiwire branch circuit. As stated by Roger you can use a 3Pole breaker or sp breakers with handle ties.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
It sounds as though the customers engineer wants his preference, not what is allowed.

Was this included in any job specs?

Roger
 

480sparky

Senior Member
Location
Iowegia
If MWBCs weren't allowed any more, they would have been written out of the Code. But clearly, they're still there, so they are allowed.

210.4 merely states how MWBCs are to be handled.... it doesn't say you can't have them.

If MWBCs ever become 'illegal', I don't know what we'll do to supply power to all these residential electric ranges, cooktops, ovens and clothes dryers.
 
But is it required to use either the three hots with three neutrals "or" a three pole breaker or single poles with a breaker tie?
 

jusme123

Senior Member
Location
NY
Occupation
JW
If MWBCs weren't allowed any more, they would have been written out of the Code. But clearly, they're still there, so they are allowed.

210.4 merely states how MWBCs are to be handled.... it doesn't say you can't have them.

If MWBCs ever become 'illegal', I don't know what we'll do to supply power to all these residential electric ranges, cooktops, ovens and clothes dryers.
Poor examples of the MWBC the OP is referring to. Those are two pole ckts to individual UL listed units which MUST be run on two pole breaker, no exceptions (residential), maybe three pole for commercial.
 
Last edited:

480sparky

Senior Member
Location
Iowegia
Poor examples of the MWBC the OP is referring to. Those are two pole ckts to individual UL listed units which MUST be run on two pole breaker, no exceptions (residential), maybe three pole for commercial.


Read the definition of a MWBC:

Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.


All the circuits I listed fit that definition.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Poor examples of the MWBC the OP is referring to. Those are two pole ckts to individual UL listed units which MUST be run on two pole breaker, no exceptions (residential), maybe three pole for commercial.
Actually those are good examples of MWBC's regardless of what is connected to them.

Roger
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
3 ungrounded and 3 grounded conductors sounds more like 3 regular circuits than a MWBC. One of the main reasons for a MWBC is to save on wire. If the 3 ungrounded conductors are feeding different outlets why not just use 3 individual breakers? I wouldn't want one circuit tripping and shutting the other two down. IMHO!
 

hurk27

Senior Member
3 ungrounded and 3 grounded conductors sounds more like 3 regular circuits than a MWBC. One of the main reasons for a MWBC is to save on wire. If the 3 ungrounded conductors are feeding different outlets why not just use 3 individual breakers? I wouldn't want one circuit tripping and shutting the other two down. IMHO!

With handle ties you likely wont have that happen, but also you might not know which one tripped as the other two will hold the handle in the on position and not let it go to the middle.

I believe the OP should let the customer and the engineers Battle this out, as this is a design choice not an installation problem, as was said it can be done 3 ways.
 

jusme123

Senior Member
Location
NY
Occupation
JW
Actually those are good examples of MWBC's regardless of what is connected to them.

Roger

I simply stated they where poor examples of MWBC that the OP was referring to (he is talking about 2 or more single pole ckts sharing a neutral, not a two pole dryer ckt)
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Poor examples of the MWBC the OP is referring to. Those are two pole ckts to individual UL listed units which MUST be run on two pole breaker, no exceptions (residential), maybe three pole for commercial.
Take the dryer for example, it utilizes a two pole MWBC and can use handle ties or a multi-pole breaker, a "two pole" breaker is not mandatory for this circuit, see 240.15(B)(2)

Roger
 
Last edited:

jusme123

Senior Member
Location
NY
Occupation
JW
Can a MWBC be tied to a 15 amp and a 20 amp ckt breakers ( utilizing handle ties), if 12 awg is used?
 